What is the recommended standard, connecting the arrestor earth and the transformer tank earths together or seperate?
Reply With Quote
  #2  
Old 05-24-2006, 03:23 PM
topgroove's Avatar
topgroove topgroove is online now
Senior Member
 
Join Date: Aug 2002
Location: Buffalo
Posts: 1,569
Default

here at national grid on a wye system there bonded together on a delta system they're seperate
Reply With Quote
  #3  
Old 05-25-2006, 06:52 AM
Squizzy Squizzy is offline
Senior Member
 
Join Date: Apr 2005
Location: Western Australia
Posts: 835
Default

Ours are always together, the surgies are mounted on the TX and connected to earth via the earth stud on the transformer tank. (all our HV is in delta)
Reply With Quote
  #4  
Old 05-25-2006, 07:02 AM
thrasher thrasher is offline
Senior Member
 
Join Date: Jul 2003
Location: Virginia, USA
Posts: 331
Post arrester grounds

If it's a tank mounted transformer arrester then we ground thru the stud on the txf to the txf ground loop. If it's an arrester on an OCR or x-arm mounted then it's grounded independent of other equipment. Our system is all grounded wye.
Reply With Quote
  #5  
Old 05-25-2006, 08:04 AM
topgroove's Avatar
topgroove topgroove is online now
Senior Member
 
Join Date: Aug 2002
Location: Buffalo
Posts: 1,569
Default

on ungrounded delta's the engeneers have found that current from a lightning strike can enter the customer mains and do a lot of damage in a blink of the eye. that's why we keep them separate. On a multi grounded wye the arrestors are bonded together with the stytem nuetral.
Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
 
Forum Jump


All times are GMT -5. The time now is 11:48 AM.


Powered by vBulletin® Version 3.6.9
Copyright ©2000 - 2010, Jelsoft Enterprises Ltd.

Lineman Forums at www.powerlineman.com are open forums for the free exchange of ideas and opinions for anyone using them. Any opinions expressed on these forums are not that of Powerlineman.com, LLC.