This is how the secondary is hooked up and the voltages that you would have:
The transformer on the left is a 240/480 and the coils are paralleled to give you 240.
The other 2 transformers are 120/240 and their coils are in series.
Opps, I see I put 2 B-phases in the picture, forgot to change the primary letter when I copied the picture over. Should be A - B - C
Last edited by Tester; 01-18-2012 at 11:55 PM. Reason: Wrong Primary Label
Good information, Thanks
That's something wtdoor talked about awhile back in the past. Ability to use a 240/480 transformer in a 120/240 bank--just parallel the coils.
That diagram shows the wye grounded on the highside...maybe to close in, but I'd float once it's closed in - you'll burn a transformer up.
Hey Tester welcome aboard bro! I'm glad you joined the forum. We all appreciate your knowedge around here!
This will probebly have a few people scratching their heads. That last bank schematic, if you leave the float grounded after its energized....... I could open one of those cutouts and the customer would never know the difference as long as their load was reasonable.