    Make you a deal. I come to Ok, you feed me both food, beer and knowledge and I'll give you a Dallas Cowboy's hat since I know deep down inside you wish you where south of the Red River.

  2. #12
    Join Date
    Jan 2008
    Location
    usa/ Oklahoma
    Posts
    2,221

    Default Heh.

    Sooner go to Mexico.

  3. #13

    Default

    Quote Originally Posted by johnbellamy View Post
    Good info and picture, simple and strait forward answer, a good rerferance for all to see. Real life and it jumps off the screen right at ya, thanks for thread, now nobody **** it up by confusin anyone.

    Would have been nice to know what the primary voltage was also, name plate info as far as primary, not that it really matters with this one, and before anybody brings up the 4 bushing secondary pots, please post pictures, and start a new thread and please explain what parallal and series mean and then post and discuss till ya can't type. Thanks
    OK..makes sense now. Thanks for all the help.

    And the primary is 7kv delta.

    HP

  4. Default

    Quote Originally Posted by HIPotter View Post
    This bank of transformer is scheduled for removal.

    Primary is/was a Delta connection
    Secondary service is 120/240 3 phase 4 wire

    Both outside pots are 75kva, middle pot is 100kva

    Here's the deal, left outside pot is 230/460, and other 2 pots are 110/230 per nameplate.

    The way it's wired, I don't understand how it gives you that secondary voltage.

    Any transformer guru's here?

    Hopefully the attachment shows a clear enough picture

    HP
    This is how the secondary is hooked up and the voltages that you would have:
    The transformer on the left is a 240/480 and the coils are paralleled to give you 240.
    The other 2 transformers are 120/240 and their coils are in series.
    Opps, I see I put 2 B-phases in the picture, forgot to change the primary letter when I copied the picture over. Should be A - B - C
    Attached Images Attached Images  
    Last edited by Tester; 01-18-2012 at 11:55 PM. Reason: Wrong Primary Label

  5. Default Dogman

    Good information, Thanks

  6. #16
    Join Date
    Jul 2007
    Location
    Fort Worth
    Posts
    638

    Default

    That's something wtdoor talked about awhile back in the past. Ability to use a 240/480 transformer in a 120/240 bank--just parallel the coils.

    That diagram shows the wye grounded on the highside...maybe to close in, but I'd float once it's closed in - you'll burn a transformer up.

  7. Default Agree - Float the high side

    Quote Originally Posted by rcdallas View Post
    That's something wtdoor talked about awhile back in the past. Ability to use a 240/480 transformer in a 120/240 bank--just parallel the coils.

    That diagram shows the wye grounded on the highside...maybe to close in, but I'd float once it's closed in - you'll burn a transformer up.
    I agree that the primary should be floated after all the cutouts are closed.
    I was trying to emphasize the secondary connections.

  8. #18
    Join Date
    Aug 2002
    Location
    Buffalo
    Posts
    3,000

    Default

    Featured Sponsorr

    Quote Originally Posted by Tester View Post
    I agree that the primary should be floated after all the cutouts are closed.
    I was trying to emphasize the secondary connections.
    Hey Tester welcome aboard bro! I'm glad you joined the forum. We all appreciate your knowedge around here!

    This will probebly have a few people scratching their heads. That last bank schematic, if you leave the float grounded after its energized....... I could open one of those cutouts and the customer would never know the difference as long as their load was reasonable.