Page 1 of 2 1 2 LastLast
Results 1 to 10 of 14
  1. #1

    Default 4th cut out on wye delta banks

    Featured Sponsor

    I was wondering if anyone had a technical drawing (i.e. print) that I could share with our engineers here at CVEC that shows the installation of the 4th door for the neutral float on the high side.

    any help would be appreciated. I'd really like it if some one could provide such a drawing in reference to a corner grounded delta.

    Thank you and

    work safely,

    L.A.Martin
    Journeyman Div III
    CVEC
    Last edited by LAMartin.CVEC; 08-05-2012 at 06:20 PM.
    There's no such thing as "The End Of The Line!"

    If you think you are worth what you know, you are very wrong. Your knowledge today does not have much value beyond a couple of years. Your value is what you can learn and how easily you can adapt to the changes this profession brings so often. -- Jose M. Aguilar

  2. #2

    Default $th cut-out

    Never heard of such a thing on a wye delta bank all thou I guess it wouldn't be bad if ya could find room.I guess ya would leave it open and load side tapped to floated H2.The other end tied to ground.Like i said door open thou unless ya need to operate the bank as an open bank.I think i would rather just use a shotgun and a ground jumper to tye er down thou,as this is only temporary conditions or ya could burn up the bank.

  3. #3

    Default

    i have seen several of these banks, you find them alot in the irragation areas, alot of times they send out a single man to energize/de-energize the banks before and after the irrigation season, its alot safer and easier when the bank is put in and out of service. usually the higher the voltage the greater the chance of having problems with the floating h2 while fusing, ground the float with the 4th cutout, open or close the other 3 and open the 4th back up and there ya go.

  4. #4
    Join Date
    Jun 2011
    Location
    West / south / wherever
    Posts
    133

    Default

    we just tie the h2's together and keep it running to the top of the cut out that is usually installed on the transformer bracket or sometimes on the pole. the bottom of the cutout goes to the pole ground...never seen a drawing for it though...

    anybody ever seen one of these bank blow up or other damage occur from not tying down the h2's?

  5. #5

    Default

    Quote Originally Posted by Bighorn Ape View Post
    we just tie the h2's together and keep it running to the top of the cut out that is usually installed on the transformer bracket or sometimes on the pole. the bottom of the cutout goes to the pole ground...never seen a drawing for it though...

    anybody ever seen one of these bank blow up or other damage occur from not tying down the h2's?
    We just have problems with them blowing the lightning arrestors, ground down the floating neutral on the high side temporarily with the 4th cutout close in the bank open cutout and no blown arrestors, first time I ever saw this was on a closed delta overhead bank that was being fed by URD primary. It was common practice not to ground down the floating neutral temporarily where the primary voltage was 7200 or 7620 as it didn't seem to be a problem until you had higher primary voltage such as 14.4 or the rare URD feeding the overhead bank, at least down here where I'm at.There are a few utilities down here that have the 4th cutout as part of their standards, we have always only installed them on the few banks that gave us trouble.

  6. #6

    Default Cur-out

    We never install a cutout on the floated wye delta closed bank.Always just floated the H2.If we need to operate the bank as an open bank then you would tie the floating neutral down.The only time we would have a lightning arrester blow would be on a fused line that feeds a wye delta bank like this.The reason is because you have a back feed from the delta on the wye delta bank.This puts an opposite voltage at your blown fuse.When you close in the fuse you will here the arrester blow @ the bank because of the spike in phase to phase voltage at the blown fuse.The voltage is higher than what the arrester is rated for.We have gone to an 18kv arrester on all fused lines.A 10 kv rated arrester exceeds the phase to phase voltage you have.It maybe instantaneous until the delta collapses .This solves the problem.Other wise you would have to isolate the arrester @ the bank.Close the fuse, then tap the arrester on.On 3phase lines you dont have this problem,only on a fused line.Most of our feeder lines have 3 phase breakers.

  7. #7
    Join Date
    Oct 2006
    Location
    South East Texas
    Posts
    3,278

    Default

    UMMMMMMMM LA we always just ran a lead from the floating primary buss to a cutout and hooked the hi side of that cutout to either the pole ground or the system neutral ,whichever was most accomodating. Some use a bladed rather than a fused disconnect. I suspect its the resident engineers call. We only did that on voltages above 13.2 K to combat ferrosresonance, And the Lightening arrestors are the least of your problems ,I have seen entire transformers blow a lid off without the use of that 4th cutout.

  8. #8

    Cool groundn' switch

    4th c/o {grounding sw} we mount on pole bkt. back side of bank. reminder never close switch if you have open c/o bobcat delmarva pwr.

  9. Default Dogman

    We put up a 10 ft x-arm, and put a solid blade cut-out on it. With the 3 other cut-outs. Had a wye/ corner grounded delta going to a seed cleaning company. Mat. man re-fused blown fuse with out grounding high side, burned up 3 transformers and kicked 1 Ø off at the OCR's. Bob

  10. #10

    Default

    Featured Sponsorr

    bump

    I'm still looking for a "print" to share with my engineering department
    There's no such thing as "The End Of The Line!"

    If you think you are worth what you know, you are very wrong. Your knowledge today does not have much value beyond a couple of years. Your value is what you can learn and how easily you can adapt to the changes this profession brings so often. -- Jose M. Aguilar

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •