    Default 120/120/0 + load readings

    If you test at the pedistal or Transformer on this run you can have 120/120/240 but you know you have 120/120/0 at the meter or entrance. At the source test the amp draw one leg will have load (total load) and the other will have a zero (very low) reading. Then at the entrance you can do the same thing and you will find the good leg (it will have load) and the other will be zero. You could disconnect the no load leg and then test the lead and find the 120 is gone. If you test across the entrance terminals you will get a 120/120/0 Now you know the 240 volt equipment was backfeeding the false 120volt reading you originally had. Now if the customer is not in big need of the 240 (for a well or sump or electric heat) you could see if they can live till the next day on 120. You can open the water heater circuit and A/C circuit, install a temp jumper in the entrance and they would have lights and refer. . . if the load is not too high for a jumper. It's a judgement call and maybe your outfit would not allow. . .just a sugestion.