  1. #1

    Default ground rods

    ............Here we usually use 1 ground rod on our 12kv dist. circuits.............transformer poles get 1 ground rod and plain inline poles we butt bond them............on our 34.5 system we use 2 ground-rods on every pole...........same with urd........12 kv 1 grd. rod.......34.5 2 grd.rods.................now when I was in southern Flordia,we only worked urd..........if Im not mistaken they wanted 8 grd rods on there urd.......we had to (ohm) them and place a tag near the ground rod........any replies on rods?..wondering if Flordia is the only area where they want 8.

  2. #2
    Join Date
    Feb 2007
    Location
    Ontario Canada
    Posts
    1,284

    Default

    On transformer poles we need 1 ground rod 18" from the pole meggerd to at least 25 ohms & #4 cu run up the pole, for risers it is the same except 1/0 cu. For all U.G. we need 4 ground rods 1 at each corner again meggered to 25 ohms & grounded with 2/0 cu & if there are bullards they also have to be bonded to the 2/0. On our 44kv load break switches we need 3 ground rods again with 1/0 cu run up the pole.
    Last edited by lewy; 02-04-2012 at 11:45 PM.

  3. #3

    Default are you saying

    Quote Originally Posted by lewy View Post
    On transformer poles we need 1 ground rod 18" from the pole meggerd to at least 25 ohms & #4 cu run up the pole, for risers it is the same except 1/0 cu. For all U.G. we need 4 ground rods at the corners again meggered to 25 ohms & grounded with 2/0 cu & if there are bullards they also have to be bonded to the 2/0. On our 44kv load break switches we need 3 ground rods again with 1/0 cu run up the pole.
    lewy,are you saying that you guy put 4 ground rods on all 4 corners of the urd pot,and Im interested in where you are located..........what type of earth,rocky,sandy,gumbo,ect

  4. #4
    Join Date
    Feb 2007
    Location
    Ontario Canada
    Posts
    1,284

    Default

    We have all different kinds of soil except obviously we don't put transformers in swamps or mud bogs. I edited my original post.

  5. #5
    Join Date
    Dec 2010
    Location
    Ontario, Canada
    Posts
    1,012

    Default

    A couple of utilities here have changed there standards to allow ground plates to be used instead of rods. Really handy in rocky ground or in the city with congested underground utilities.

  6. #6

    Default

    We use 5/8"X10' ground rods, #6 cu. for wire. All transformer pole mount or pad mount get 1 ground rod, all urd riser poles 1 ground rod, all arrestor poles 1 ground rod. All rods must test 25 ohms or less if not keep adding rods 8' from the existing one until it test properly, if conditions will not allow moving away from the pole or equipment then add coupling and more rods as needed.
    All other poles except for corner structures will get a butt plate.
    We are lucky to have good soil conditions and moisture.

  7. #7

    Default rob?????????

    Quote Originally Posted by rob8210 View Post
    A couple of utilities here have changed there standards to allow ground plates to be used instead of rods. Really handy in rocky ground or in the city with congested underground utilities.
    Guess I could have googled this..............but what the heell is a ground plate,can you explain what it is and how its intended to work..........barley lost...