  1. #31

    Default

    Featured Sponsor

    About the only place the running ground is used in Ct is when doing transmission work or when running the messenger for spacer cable all new conductor is usually tree wire/spacer cable. The Hubble type is preferred method,tying all grds together and going to system neutral also preferred, but because of lack of knowledge on the part of supervision and trying to save a buck don't always have grd mat Co. says ok to stand on rubber blanket on top of piece of plastic, insulate isolate ?

  2. #32
    Join Date
    Dec 2010
    Location
    Ontario, Canada
    Posts
    1,012

    Default

    We have a generally accepted practice around here regarding grounding and bonding of equipment for stringing . Ground gradient mats under the tensioner with double barrier fencing. Machines grounded to the system neutral( when possible), conductor grounded with a reel ground and maybe a travelling ground(depending on type of conductor). Travellers grounded at first, last , before and after any live crossing and somewhere between every 5 to 7 spans. Do you get your conductor on steel or wooden reels?

  3. #33

    Default Stringing conductor

    The reel trailer is grounded,the Wire is grounded with a Hubble rotating ground attached on the very end of the wire coming out of the wood reel that is bolted to the reel shaft.Then another ground is attached to the same rotating Hubble reel bearing that rotates on the reel shaft which is connected to the system neutral.We do not use mats,just rubber gloves and stay isolated from reel.The tensioner on the other end is grounded also,breaker one shot.When the wire reaches its destination its ground as we go till all are pulled in and grounded.Sagging is done on the least hazardous end.If its a long pull then we will ground again accordingly in the middle or just rubber glove tying the conductor in.
    Birdog37: "Remember we're all on a journey in life, the only difference is, some people know it and some people don't."

  4. #34
    Join Date
    Feb 2007
    Location
    Ontario Canada
    Posts
    1,284

    Default

    I really don't understand why mats are not used when tension stringing over or near energized conductors. Doesn't take that much longer to back the tension trailer on to the mat and set up a proper EPZ, the only safe way to eliminate step and touch potential, especially when you have to change reels and sleeve onto the wire already strung in.

  5. #35

    Default Use a grounding block at your takeoff.

    You are aloud to use a grounded block at your take off in lieu of a rolling ground. At the dead end you can go under the hazard if hot primary and protect the guys on the wire cart. When we had a broken rolling ground, that's doing the same thing. As long as a ground is installed between the brake over and the cart. If it's just a three phase primary pole, it's the same thing as a traveling ground. Except the bomb of phase to ground is going to happen at the block not near the wire cart.

  6. #36
    Join Date
    Feb 2007
    Location
    Ontario Canada
    Posts
    1,284

    Default

    The reality is the only way to really protect the men if sh*t hits the fan at the tensioner (wire end) is to set up a proper EPZ with mats and proper bonding, anything less is just a false sense of security. You don't want the fault clearing at the tension machine you just want everything staying at the same potential while the fault clears.

  7. #37

    Default Equall potential

    Featured Sponsorr

    Makes good sense to use the mats.Just never used them.Will bring this up at our next safety meeting.Thanks for info.