I guess the best bet would be a suitable high voltage tester that could test the unit to it's rated voltage and beyond to see if it was perhaps flashing over inside.
Deep down you're HOPING it's the transformer and not the URD.
What is your procedure to test a step down that you suspect is cause of outage. Scenario:Over head step down TX feeding underground primary with 8 urd tx,s
Linemanblood
I guess the best bet would be a suitable high voltage tester that could test the unit to it's rated voltage and beyond to see if it was perhaps flashing over inside.
Deep down you're HOPING it's the transformer and not the URD.
Portable defibrillators were first invented to save the lives of linemen. Where's yours?
www.bigclive.com
We used to clear the low side and try a fuse. Now I think they use a HI-POT tester.
National Grid = Retired! US Army vet. 68 - 70
As of April of 2010 I quit smoking! It's been hard but so far no butts! I am now an X smoker!
best bet is to have a fuse on the high and low side.that should be a good start to find the problem,assuming the fuses are the proper rating.
lineman641
we just got these new TILT (Transformer Initial Living Tester) testers. It's got two probes go from bushing to bushing. Tests for open and shorts, Tests Capacitors too...only thing that sucks is when the xformer is on the pole you have to remove everything (especially the pot ground) to use it. A definite time saver and keeps you from putting up a bad pot if you use it in the morning when loading up.
Don't put all your faith in the TILT. Mine has lied to me on more than one occasion. Be sure and take everything loose including the lightning arrestor. A bad arrestor can show up as a short.