This bank can be changed from a 240 delta to a 120/208 wye. You would just have to parallel the secondary windings to make each transformer 120, or ground the x2 and turn each transformer back to 120/240 and just use 1 leg from each transformer, but you would only get half the KVA of each transformer.
Depending on how you hook it up you either get 225KVA or 112
Take the lids off and split the pots, AC/BD leaving one bushing as you're dummy bushing, surely FP&L has a standard spec for which bushing is you're dummy bushing I would think, not real sure why someone would tell you that it could not be done unless there is something else that I'm not seeing.