    Default Pole mounted metering units

    Hi,guys.We install two types of metering units on poles;all have three bushings on the line side and some have three or two bushings on the load side of the unit.I was asked when do we use one as opposed to the other and honestly could not say as I have seen them installed as they are available.I was told thet the 3/3 bushing types are for Y-Y systems and the 3/2 are for wye-delta installations.Reason being,if the three phases are balanced,the third one goes from line to load without being metered as it is assumed that is equal to the two that are metered.Can I have an perspective on this?Much appreciated!

  2. #2

    Default

    Get pictures of this device and/or the form numbers of the metering.
    We would never assume a customers load is balanced, you never when they change loads.

  3. #3
    Join Date
    Oct 2002
    Location
    Arizona
    Posts
    47

    Default

    only balanced if all single phase ( V phase) loads are balanced to the load side

  4. #4
    Join Date
    Dec 2002
    Location
    Bridgetown, Barbados, Barbados
    Posts
    118

    Default

    I agree,Trigger.And we know that the engineers plan for one thing,the business owners do something else.So it would make sense to have a unit that meters all three phases and that brings me to what the real issue is;cost.I understand the metering units are tens of thousands of dollars but the 3/2 configuration is cheaper.I just want to know if the two configurations are interchangeable between wye-delta and wye-wye.Thanks for the response,will see if I can get a photo or two.

  5. Default

    On the secondary side of the bank...

    We used only two ct's on pump banks, wye-wye and wye-delta(closed). These banks only fed irrigation pumps so balanced loads were just about guaranteed.

    We also used one ct on 1phase services.

    We've moved to three on all three phase installs and two on all single phase. Wye-wye or wye-delta.

    Primary metering packages were always one ct, one pt on single phase and three ct, two pt on three phase. Two phase line got two and two.

    Wow, going back in time there 1980's!

  6. #6
    Join Date
    Oct 2002
    Location
    Arizona
    Posts
    47

    Default

    Then the customer figures this scheme out on the sec. side and adds 1 ph load onto the unmetered leg and gets free power